FabyaVisionUser Manual
/

Simulator driver

4 min readCommunication

Built-in driver whose address is a signal generator, for designing and trying out screens and giving presentations without a PLC: sine, ramp, square, random, counter and constant; also manually changed values.

When to use it

The simulator is a driver that runs inside Live; it requires no network address or port. The address of the tag is a signal generator: while Live is running, the tag value is updated with the value produced by this function. It is used to try out a new screen without connecting to a PLC, for training and presentations, and to see trend and alarm behavior. The quick start and the sample project use this driver (Your first project).

Setting up connections and tags

  1. Add a connection

    In the Connections section: Add, driver Simulator. The IP address and port cells are locked; there is no driver parameter. In Live, the connection is always in the Simulator state.

  2. Add a tag

    In the HMI tags section, create a tag bound to this connection and select its data type (Bool, Byte, SInt, Int, UInt, DInt, UDInt, Real, LReal).

  3. Enter the signal

    Enter the function in the Address cell: sinus(20, 80, 60). A description of the signal appears below the cell; an incorrect entry is not accepted.

    Simulator tags: the functions in the address column define the signal; the address resolution of the selected tag appears in the Inspector.12
    Simulator tags: the functions in the address column define the signal; the address resolution of the selected tag appears in the Inspector.
    1. Address — in the simulator, the address is a signal function.
    2. Address resolution — the description of the signal.

Signal functions

Numbers can be written with a decimal point (0.5); the function name is case-insensitive. Time is the number of seconds elapsed since Live started.

FunctionGenerated value
sinus(min, max, period s)A sine wave oscillating between the minimum and the maximum; it starts at the middle of the range.
rampa(min, max, period s)A sawtooth that rises linearly from the minimum to the maximum in every period and then returns to the minimum.
kare(min, max, period s)A square wave that gives the maximum value in the first half of the period and the minimum value in the second half. On a Bool tag, if the maximum value is 1, it is on in the first half and off in the second half.
rastgele(min, max)A random value within the range on every update.
sayac(min, max, step time s)A counter that increases by 1 every step duration and returns to the minimum when it reaches the maximum.
sabit(değer)Always the same value.

Rules: the min value must be less than the max value, and the period and step time must be greater than zero. The driver converts the number to the tag type: for Bool, 0.5 and above is on; for Real / LReal it is rounded to 3 decimal places; for integer types it is rounded to the nearest integer.

Manually changed value

If the address is left empty, the simulator tag does not generate a signal; its value starts with the Start value and is changed by being written by the operator or by a script while Live is running (control button, I/O field, script). If a simulator tag with a signal is written to, the signal stops from then on and the tag stays at the written value; the signal starts again when Live is reopened.

Tips and limits

  • The signal is updated at the interval of the tag's read cycle; Live applies at least 100 ms. To put fast- and slow-changing signals in different cycles, use the Cycles table.
  • The simulator value is treated as a raw value: if scaling is on in the tag, the generated value is scaled. T101_Seviye in the sample project (sinus(9400, 25160, 80), raw 0 – 27648 → 0 – 100 %) works this way.
  • The quality of a simulator connection is always good; the substitute value setting is never used.
  • When you move a ready-made project to a real PLC, you do not change the connection but the connection of the tags and their addresses: update the Connection and Address columns in the tag table; for many tags, export the table to Excel, edit these two columns and import it back (Transferring tags with Excel).

Related topics